Problem with Carrier Ultra XTC

Discussion in 'Refrigerated Trucking Forum' started by ltzSupra, May 30, 2016.

  1. ltzSupra

    ltzSupra Bobtail Member

    37
    27
    Feb 25, 2011
    0
    I just got into the reefer scene about a month now, bought a 2006 3000R with a Carrier Ultra XTC, its an ex Marten trailer. I noticed that I don't hit the set temp on continuous mode, only on start and stop. Same thing loaded or empty. Has anyone experienced this before or knows what I need to do to get this corrected? Any input will be greatly appreciated.

    Continuous - This is the lowest box temp I will get on 36 degrees
    20160530_154012.jpg

    Start/Stop
    20160530_154239.jpg

    Now when it hits 36 box temp on Start/Stop and shuts off and I change it back to Continuous, it'll go into heat mode and go back up to a box temp of 39-40 box temp.
     
  2. Truckers Report Jobs

    Trucking Jobs in 30 seconds

    Every month 400 people find a job with the help of TruckersReport.

  3. STexan

    STexan Road Train Member

    14,962
    29,144
    Oct 3, 2011
    Longview, TX
    0
    At that temp around low and mid 30's the unit will "cautiously" cool so as not to risk any freeze damage of sensitive products with output air too cold. With loads that might have been stored about 40 (or warmer) it can take 36-48 hours to ever get the entire load's core stabilized and lowered and hit the set point. I've seen this before but not had any issues.

    As far as empty, this may not be an indication of anything wrong either. Others with more experience might chime in with other better explanation.
     
    Last edited: May 30, 2016
    ltzSupra Thanks this.
  4. iRookie

    iRookie Light Load Member

    140
    174
    Aug 16, 2015
    0
    I believe Protect Fresh should be turned (0-OFF) or (3-C) see page 37 of the owners manual CLICK HERE.

    For FUNCTIONAL CHANGE (PARAMETERS) goto page 34.

    If you screw up goto page 45 and reset the unit to factory defaults.
     
    Last edited: May 30, 2016
    ltzSupra Thanks this.
  5. ltzSupra

    ltzSupra Bobtail Member

    37
    27
    Feb 25, 2011
    0
    I saw something about that before, the different modes A,B,C...I'll have to check that out in the morning. I'm pretty sure this is what has to be adjusted. Thanks for the quick info!
     
  6. ltzSupra

    ltzSupra Bobtail Member

    37
    27
    Feb 25, 2011
    0
    Oo that makes sense too. I haul produce so I wouldn't want that to freeze on me.
     
  7. Balakov100

    Balakov100 Road Train Member

    3,937
    2,635
    May 10, 2012
    Temple, TX
    0
    Produce should not be run in start/stop
     
  8. ltzSupra

    ltzSupra Bobtail Member

    37
    27
    Feb 25, 2011
    0
    Changed it 0, hit 36 on continuous! Thanks for the help
     
    Onemanshow and iRookie Thank this.
  9. ltzSupra

    ltzSupra Bobtail Member

    37
    27
    Feb 25, 2011
    0
    I know that, was just trying to figure out why the unit only hit temp in that mode and not continuous. But it's good to go now that I changed the parameters.
     
  10. iRookie

    iRookie Light Load Member

    140
    174
    Aug 16, 2015
    0
    I'm happy it worked out for you.
     
  11. tayus

    tayus Bobtail Member

    18
    10
    Feb 4, 2012
    Windsor
    0
    I haul cucumbers, tomatoes, and pepper all the time, we always run on start/stop set at 50 degrees and never had a rejection from temp.
     