My old carrier ultra xtc won't get below +8 on a 85degree ambient on a -10 setting, also as I was going thru the display I noticed that my discharge pressure was above 400psi, isn't that too high, i also checked the red ball on the side and they were both floating, the bottom ball was floating 65% and the top ball was floating 40%, any ideas on where to start?
-
How long since the condenser was cleaned?
-
14 months ago
-
Randall manufacturing, I have flaps in it too so I can put refrigerated on the tail for short distances as well and still get cold air back there. Helps a lot if your doors don’t seal that good,
i was holding like -3 this week with all the 95+ degree weather,Jarhed1964 and Buckeyes614 Thank this. -
Precedent ERG is a simple fix. $100 sonic cleaner and an hour. Only need to buy new gaskets. TK says 5K hours but we just do it every service.
Jarhed1964 and slow.rider Thank this. -
Yeah too high.Leave the reefer running and wash the condenser coil for a good 15 minutes.If using a power washer dont bring the tip to close to the condensor as you might flatten the fins on it.Buckeyes614 Thanks this.