Carrier 7500 code 28

Discussion in 'Refrigerated Trucking Forum' started by 062, Aug 16, 2020.

  1. 062

    062 Road Train Member

    5,852
    31,732
    Oct 20, 2013
    0
    @reeferwrencher I want to see if you’ve come across this problem. After a defrost cycle the expansion valve goes to 20% then to 0% and then back to 20% and unit shuts off. It’ll do this about once a month and 2-3 times back to back. Is that a sign that the expansion valve is going bad or is there another cause?
     
  2. Truckers Report Jobs

    Trucking Jobs in 30 seconds

    Every month 400 people find a job with the help of TruckersReport.

  3. reeferwrencher

    reeferwrencher Medium Load Member

    552
    1,469
    Aug 4, 2018
    0
    I ve never seen that,but to my knowledge the electronic valve is very reliable. Is it cooling good otherwise? And is defrost working ok?
     
    062 Thanks this.
  4. 062

    062 Road Train Member

    5,852
    31,732
    Oct 20, 2013
    0
    Yes. I don’t know for sure that’s the cause, I just noticed it yesterday and it seems odd. I’m not able to see all the functions on the screen at one time. When it shut off I scrolled up and the suction pressure was 61.
     
  5. reeferwrencher

    reeferwrencher Medium Load Member

    552
    1,469
    Aug 4, 2018
    0
     
  6. reeferwrencher

    reeferwrencher Medium Load Member

    552
    1,469
    Aug 4, 2018
    0
    Make sure the ball is up and check plug connection on sv2.If any problem with that solenoid it will run into a vacuum right away and stop cooling
     
    KB3MMX and 062 Thank this.