After thinking about it for a bit, you could test the thermostatic switch with a pulp thermometer and a test light. Stick the probe of the thermometer in the evaporator next to the probe for the switch.
Disconnect the switch and see which side is always hot on the plug. Then reconnect it and stick your test light on the other terminal.
If the evaporator is warmer than about 32°, your test light should be lit. Start the system up and watch the thermometer go down. The test light should go out very close to 32°. If it doesn't, then your thermostatic switch is bad.
Depending on where that switch is in the circuit, you may have multiple problems if you are having to jump the trinary switch to get power to the thermostatic switch.
From the AC relay, power flows in a series circuit through the thermostatic switch and the trinary switch on its way to the compressor clutch.
If the trinary switch is first in line, then there should be sufficient refrigerant pressure to keep the low-pressure part of the switch closed and the pressure shouldn't be high enough so that the high side of the switch opens. If everything is good at the trinary switch it then sends power through the thermostatic switch and then on to the compressor.
The positions of the trinary switch and the thermostatic switch can be swapped. Either way will work.
The third function of the trinary switch is to turn the fan on when the pressure gets above a set point.
As far as the refrigerant pressures go, refer to a temperature pressure chart for R134a. But basically, on an 80° day with the AC set to recirculate and the fan solenoid unplugged so the fan stays on, you should see about 40 pounds on the low side and 175 to 200 on the high side.
1994 W900L AC Theromostat Switch
Discussion in 'Kenworth Forum' started by JimmyWells, May 26, 2017.
Page 3 of 6
-
-
Trucking Jobs in 30 seconds
Every month 400 people find a job with the help of TruckersReport.
-
-
The reason I'm thinking it's the thermoswitch is because I'm jumping the two wires that go to the center two posts of the trinary switch labeled, "A/C Thermo" and "Override". By jumping those two wires I'm fooling the circuit into believing the thermoswitch is closed and allowing the compressor to run. Am I correct? I've attached a picture of the trinary switch and diagram.Attached Files:
-
-
1. Input wire from the fan solenoid. [override]
2. Ground
When the pressure goes above 250 lbs or so, the switch between 1 & 2 closes, grounding the fan solenoid and turning the fan on.
3. Hot from thermostatic switch
4. Compressor
If the refrigerant pressure is above 20 lbs and below 350 lbs, the switch between 3 & 4 is closed, sending power out terminal 4 to the compressor.
This makes me think that KW uses a hot wire to the fan solenoid insteading of grounding it.
So... the ones labeled power and override are for the fan. There is probably voltage on the override terminal and you're sending it through to the thermostat terminal through the closed switch to the compressor terminal and on to the compressor.
If there is no voltage on the wire connected to the thermo terminal, you need to check that there is power on both terminals of the thermostatic switch. If none have power, you have a problem further up the line... a blown fuse, a bad relay or a bad AC dash switch.
If only one has power, the thermostatic switch is bad.
Now for the other problem... fluttering gauges. The gauges should be fairly steady and not flutter. What kind of gauge set do you have?
Is it only the low side, the high side, or both? If they are fluttering real bad (like 1/4 scale), your compressor probably took a hit of liquid on the suction side and busted a reed valve.JimmyWells Thanks this. -
Since we are on the subject on the amount of freon, if the dryer has a eye glass, can you still go by it, referring to stop adding freon once the bubbles clear thru the eye glass ?
-
I also noticed that the top of the two evaporator lines is always more colder than the bottom line. Does that mean there's a restriction inside the evap?
I'll look into it more tomorrow. Why would the system just stop after running for a while with no issues? Once it gets down to 38-40 degrees it shuts off and won't run again. Like I can't make it start up again by resetting with a removal of power etc etc. This has me baffled. I have no idea why it decides to start working again nor why it stops. I keep thinking abou tthe thermoswitch. At first I thought a failing relay but I've replaced the one in the kick panel fuse box with a new one.Last edited: May 28, 2017
-
Diesel Dave Thanks this.
-
Also verify that there really is no power at the compressor clutch when it doesn't want to come back on. It may be that the clutch is worn out and the air gap is too wide to pull it back in. Simetimes tapping the clutch with a screwdriver handle will get it to engage.
Harbor Freight gauges are ok, albeit the fittings are a bit leaky. I carry a set on the truck with me. If both sides are fluctuating like you say, the compressor is probably toast.JimmyWells Thanks this. -
You can also estimate when the system is fully charged by placing your hand on the outlet pipe of the evaporator. When you feel it suddenly become very cold, it is properly flooded and has enough.
JimmyWells Thanks this. -
If there's a problem with the reed valves should I replace the compressor? Seems like a shame because it does actually work still. The temps get down as low as 38 degrees from the center vent.Last edited: May 29, 2017