Hello everyone,
Hope someone can help with this issue or provide guidance on how to solve it.
I have a reefer with a thermoking unit (sb210) that works just fine when you initially turn it on, the problem comes when it reaches the temp, shuts down and turns on again. The temp will come up to ambient temp. Looks like something is getting stuck after that first cycle.
Have any of you experienced that?
Thank you for the support!
Help - Reefer not cooling after first cycle (start/stop)
Discussion in 'Refrigerated Trucking Forum' started by hmpfletes, Sep 27, 2022.
Page 1 of 2
-
-
Trucking Jobs in 30 seconds
Every month 400 people find a job with the help of TruckersReport.
-
-
Hi,
Basically it stops cooling after the first stop on cycle mode. I’ll try to explain the situation:
I set the temp to 24F, start the unit, it cools to the 24F and stops, after the re-start, temp start to increase ignoring the setpoint.
I left the unit running overnight and I got codes 21 and 26. -
-
-
Hello guys,
just wanted to follow this up. The 3 way valve was replaced and seems like it is working now. Thank you so much!
Also, another question came up, is there a way to adjust the setpoint tolerances? The following is happening, not sure if it is how the reefer is supposed to work or not:
I set the temp to lets say 24F, unit cools down to 24F and it shuts down (totally fine) but the temp keeps going down until it reaches 20F then the unit turns on and starts heating to keep the temp in 24F, it reaches 34 - 35F and starts cooling down again.
With this, the unit runs almost all the time without shutting down, not sure if the operational tolerances can be adjusted to open them up a little bit (+\- 8 F maybe?)
Any input is really appreciated.MartinFromBC Thanks this. -
-
-